Thread: Low Design Flow During Fire Flow

  1. #1

    Join Date
    Nov 2016
    Posts
    23

    Low Design Flow During Fire Flow

    I have a model whose results are puzzling. I applied a fire flow of 1,500 gpm to all Junctions along the main line and the two (2) fire hydrants. The change in elevation from pump location to the most extreme fire hydrant is +55 ft. The design flow obtained at all junctions on the main were below 1,500 gpm. I want to know what I can do to get the design flow up over 1,500 gpm. I have attached the fire flow results and an image of the model for consideration.
    Attached Images Attached Images

  2. #2
    Member
    Join Date
    Dec 2016
    Posts
    57
    Your critical nodes are J10 and J26. It would be helpful to know which are those nodes.
    Also the fireflow analysis would be helpful; to verify static pressure - residual pressure drop.

  3. #3

    Join Date
    Nov 2016
    Posts
    23
    Thank you for the reply. Nodes J10 and J126 are the Fire Hydrants on the network. The results posted above is actually the fire flow analysis.

  4. #4
    Forum Moderator

    Innovyze Employee



    Innovyze Employee



    Join Date
    May 2015
    Posts
    420
    David,

    One of the best ways to identify what parts of the system are causing excessive headloss during the fire flow conditions is to run a "manual" fireflow so that you can see results for each pipe and junction when the fire is occurring. You can do that fairly easy using the software by either manually placing a demand in the amount of the required fireflow on the junction and running a standard analysis or by using the multi-fireflow tab and simply selecting the single junction that is showing less available flow than is required. The Multi-fireflow tool will then add the fireflow demand on top of the existing demand and you can see results for every pipe and node in the system when the fire is occurring.

    This is key in identifying what the issues are because what you want to do is to find what pipes in the system are causing high headloss. Generally if you look for pipelines exhibiting velocities greater than 10 fps during fireflow conditions that is a good place to start. Generally if the fireflow run predicts less available flow that is required this means you generally need to add pipeline capacity to the system as this will reduce the headloss in the pipelines and allow the system to provide the required fireflow while still maintaining the minimum pressure specified (often 20 psi in the US). When you can see what each pipeline is doing when the fireflow is added, you can identify where the "excessive" pipeline headloss is occurring and see where the system has limited pipeline capacity and where adding a new pipe or upsizing an existing pipe will have the most impact. This is somewhat an iterative process, but using a manual fireflow is generally the typical way that most engineers determine where the problem is and how best to resolve it. One you finalize your pipeline improvements using a manual type fireflow run, you can then rerun the fireflow tool to verify the improvements satisfy the required fireflow criteria.

    One last note, sometimes certain nodes can have limited available fireflow due to the elevations of the junctions themselves (being too high for a region) or having a poorly defined search junction criteria such that one or more nodes in the search range are starting at a low pressure (say 25 psi or so even before the fireflow is added) such that this creates an unexpected limitation on what the system can provide. I would specifically check the elevations of junctions J126 and J10 as those are critical . It is likely that the elevation of J126 is much much higher than any other junction.

    Since this is a single main pipeline system with no looping, your primary headloss will occur along the primary main that comes from the pump station. But you may have a very small pipeline on one of the short loops that may also be causing an issue for just a few junctions. But to get the entire system to meet 1500 gpm, you generally will need to upsize that primary main to be either an 8 or 10 inch size to get 1500 gpm available at all locations. An8 inch line will be right at just under 10 fps at 1500 gpm while a 10 inch will be less. When you have a long distance without looping you can run out of available head when the mainline is so close to 10 fps that you may need to upsize it to achieve your goals. That much one can say even without seeing your exact model to verify just based on experience. This is likely why nearly all results are in the 1100 gpm range and not 1500. Upsize the main to ten inch to get improved fireflow.

    Hope this helps, please feel free to reply with any additional questions.

    Patrick Moore

  5. #5

    Join Date
    Nov 2016
    Posts
    23
    Thank you for your response. After checking out the pipe results, I see that the problem pipes are those that I inserted between two adjacent nodes in a double service connection. I put in a length of 1-ft together with the 8" diameter. Is there a way to insert two adjacent nodes in a double service without creating a 1ft pipe between them?

  6. #6

    Join Date
    Nov 2016
    Posts
    23
    Thank you for your response. After checking out the pipe results, I see that the problem pipes are those that I inserted between two adjacent nodes in a double service connection. I put in a length of 1-ft together with the 8" diameter. Is there a way to insert two adjacent nodes in a double service without creating a 1ft pipe between them?
    Attached Images Attached Images

  7. #7
    Forum Moderator

    Innovyze Employee



    Innovyze Employee



    Join Date
    May 2015
    Posts
    420
    David,

    You have to have at least a non zero pipe length for any model pipe, so any two nodes placed will require at lest some length of pipe. However, if those junction don't have demand, there is no reason necessarily for having two nodes even though it is a "double service connection". If there is no demand you could workaround this by putting a single junction on the main with two pipes splitting out from it. This way the main stays complete without the need for short pipes. If you had demand on the two nodes on the main you could still have two nodes just off the main, but connected by a single junction on the main itself.

    If you have further questions on this issue please let us know.

    Patrick

  8. #8

    Join Date
    Nov 2016
    Posts
    23
    The actual demand or service is at the ends of the "Y". The demands placed on the "double service" are just transfer demands on the way to the ends of the "Y". I will try both scenarios with the nodes and let you know how it works

  9. #9

    Join Date
    Nov 2016
    Posts
    23
    So I replaced the pump at the foot of the hill with one that has a static pressure of 99 psi instead of the current one with 74 psi and rerun the fireflow analysis and both hydrants recorded design flows of 1771 gpm and 1964 gpm. This just proved to me that the pressure at the connection point on the Main City Supply line is inadequate to provide fire flow to the top of the hill without some form of booster pump. Is there another option available?

  10. #10
    Forum Moderator

    Innovyze Employee



    Innovyze Employee



    Join Date
    May 2015
    Posts
    420
    David,

    By boosting the static pressure you are increasing the headloss that can occur between the pump station and the fire while still maintaining 20 psi. The other option you have is essentially to upsize your main from the pump station to the point you are testing.

    For example. original static pressure is 74 psi before the fire. This means you have 74-20 or 54 psi of headloss you can handle at your required flow before you have an issue. This headloss would occur in 2 places a) From the source system up to the pump station itself and b) from the pump station to the point of the fire. You usually can run a flow test before the pump station to see how going form normal demands to the fire demands would lower the suction pressure at the pump station and you can then (if you don't have the rest of the system) account for this by using a GPV between the reservoir and the pump suction. This valve would have zero headloss at zero flow but would increase to the value identified in the field when flow testing. You should generally try to eyeball the curve so that the headloss curve looks exponential rather than a strait line form zero to the maximum as the headloss will increase exponentially as the flow increases.

    One you have that curve your remaining headloss represents what happens from the pump to the test point of where you are concerned. If you get too much headloss at your required fireflow then the only way to reduce the headloss is to a) increase the pump size of your fire pump or regular pumps to account for the headloss during fireflow or to increase the pipe capacity (make them larger) so that there is less headloss at higher flows. Generally it is easiest to increase the pipe capacity. For a long strait length of pipe like you have 8 inch at 1500 gpm would generally burn too much head too quickly and so you may need to upsize all or part of the line to a 10 or 12 inch line or find some way to create a loop of 8 inch lines to allow the fire flow to come from both directions of the pipe. Increasing the pump size is much more costly especially if the pump station already exists.

    If you ran the fire without the booster on you still "could" have enough system head if you increase the pipe size of the main, which is something you would want to check first. You also need to make sure how much system headloss occurs before your subdivision is accounted for as well as this could be significant to your final recommendation. Ideally, you want to supply normal and fireflow supply without a pump and if you can this is generally preferred as fire pumps have very specific requirements such as being a specific fire pump and often have back-up power requirements so just make sure you are checking everything...

    hope this helps a bit.

    Patrick