Pump control precedence
Which has precedence: the "pump control" or the "Variable speed pump control"? I am defining both control and I don't know which will act first and in another scenario I need to disable both controls, I don't know if the "disable" option in the "Pump Control" window will disable both.
-
August 14, 2015, 09:53 AM
#2
Member

When pump is on, VSP control has a higher priority than simple pump control. When pump is off, VSP control does not apply.
To disable VSP control, change to Non-VSP in VSP control dialog; to disable pump simple control, use the disable option in the simple control dialog. So you have to disable vsp control and simple pump control separately.
-
August 17, 2015, 05:54 AM
#3
Thanks
Thanks for your answer. Help me a lot!